Hi everyone,
I built this electrical system myself and thought that I had everything wired up correctly. But last week I ran into an issue that I didn't think would happen.
Attached is a simplified wiring diagram of how I have my inverter wired up. If you need any more details please let me know.
So the situation was I plugged in a regular 125V AC/1875 watt blow dryer into my inverter for my girlfriend. She turned it on and used it for about 5 seconds until it shut off. I realized a fuse was blown somewhere as none of my 12V electronics were working.
I thought this was strange as I had a circuit breaker on the inverter and thought that should have stopped it from going any further down the line. But since my fridge also wasn't working, I knew a fuse further down the line had blown.
It turns out that the 60A mini ANL fuse right before the battery had blown but the 150A circuit breaker did not trip.
Could someone help me figure out why that 60A fuse blew and the circuit breaker didn't trip?
Side note: (I know that Renogy recommends having (2) 170Ah batteries minimum for the 3000w inverter. I plan on getting another soon. Not sure if this contributed to the issue.) Also, I can't exactly recall, but I believe all wires are either 8 or 6 AWG. All wire distances are less than 6 ft.
Thanks!
Jim
I built this electrical system myself and thought that I had everything wired up correctly. But last week I ran into an issue that I didn't think would happen.
Attached is a simplified wiring diagram of how I have my inverter wired up. If you need any more details please let me know.
So the situation was I plugged in a regular 125V AC/1875 watt blow dryer into my inverter for my girlfriend. She turned it on and used it for about 5 seconds until it shut off. I realized a fuse was blown somewhere as none of my 12V electronics were working.
I thought this was strange as I had a circuit breaker on the inverter and thought that should have stopped it from going any further down the line. But since my fridge also wasn't working, I knew a fuse further down the line had blown.
It turns out that the 60A mini ANL fuse right before the battery had blown but the 150A circuit breaker did not trip.
Could someone help me figure out why that 60A fuse blew and the circuit breaker didn't trip?
Side note: (I know that Renogy recommends having (2) 170Ah batteries minimum for the 3000w inverter. I plan on getting another soon. Not sure if this contributed to the issue.) Also, I can't exactly recall, but I believe all wires are either 8 or 6 AWG. All wire distances are less than 6 ft.
Thanks!
Jim