Not familiar with that midnight solar METER Does it use a big shunt On negative battery cable? If not, % displayed not to be trusted.
The powermax will generate a lot of heat producing 40+amps. Ventilation very important. Recirculating 120 f air will trigger thermal protection and shut down. Cross ventilation so fan can suck i. Fresh air if enclosed.
Non adjustable voltage standard 3/4 stagepowermax will drop to 13.8v as soon as maximum amps gets output terminals to 14.4. Not good for generator.
Adjustable voltage model seeks voltage pre chosen.And holds it as long as 115vAC is provided.
I only recommended adjustable voltage unit. The 3/4 stage models no good for generator charging.
cant recommend powermax anymore anyway, adjustable or not. Too many failure reports.
Check voltage at output terminals when you think it shuts down. If solar can hold battery @ 13.8v+ on Its own at that point, automatic 3/4 powermax will shut down.
Need to know voltage and amps flowing at that elecrical pressure to know what is going on regarding function and battery state of charge.
Without that info.... blind and deaf.