Please take note that the electrical crimpers you used yield a very poor crimp, both in terms of physical connection as well as electrical connection.
A shame because you used those nice crimps with the heat shrink insulation built in.
Monitor the connections for heating, and give that cheapo crimper to an enemy.
All connections introduce measurable resistance and possible failure points, so a goal should be minimizing the amount of connections and those that are necessary need to be done well with a good tool. Fuses also introduce resistance.
http://www.pbase.com/mainecruising/fuse_voltage_drop
So there is consequence to overfusing.
While you have a lot of solar for a little battery and the extra resistance should not be a deal breaker, it will increase over time and could be dangerous to the controller if a connector lets go.
One should avoid disconnecting the solar controller from the battery while the panels are generating. I try and do so only at night, and I only do so to reset my Blue Sky IPN pro remote battery monitor which gets its 12v power from the solar controller.
If your batteries are flooded, a good glass turkey baster style hydrometer should be used to verify that when the solar controller goes from absorption to float modes, that the Specific gravity was maxed out at 1.275 or higher( depends on battery) or nearly so.
This is the biggest issue with solar, and most charging sources which automatically reduce voltage when they believe the batteries are full. They are simply wrong most of the time, and the battery in most all cases needed more time at absorption voltages, and perhaps higher Absorption voltages too, and this neutered charging profile does so at the cost of battery performance and battery life.
Beware of blinking and soothing green lights. They are a marketer's best friend and the enemy of the engineer. They hydrometer is the best tool a flooded battery operator has and will often reveal shockingly low Specific gravity when both the solar controller has reverted to float and the battery monitor agrees.
AGM's are a bit more difficult, and amps hours out vs amps hours back in, as well as amps accepted by the battery at absorption voltages are ways to know when the AGM is in that 99%+ range.
Lifeline AGM battery has a "reconditioning" procedure that is similar to a flooded battery equalization charge, designed to restore capacity on chronically undercharged batteries. Lifeline's battery PDF is among the best manuals out there concerning battery charging, AGM or flooded.
http://www.lifelinebatteries.com/manual.pdf
But in the end batteries are only rented, and the effort to maximize their life might not be worth the extra effort to many. But awareness and suspicion and verification that they are possibly being chronically undercharged by charging sources, that love to display those soothing blinking or steady green full charge indicators, is the best way to insure the batteries can live upto their potential.
Of course a charge controller/source which allows one to actually fully charge a batteryvia adjustable Absorption voltage and duration is required, and most charging sources simply cannot do the job at which they claim to be proficient in doing especially before the sun gets too low to do the job and the next discharge cycle begins, which can happen often, if not daily, when a full time dweller.
Adjustable Absorption voltage and duration, validated with a hydrometer is the key. Ability to achieve equalization voltages is also a huge battery life extender, and is more important to do when batteries live their life undercharged.
I can reprogram my solar controller to do 16V, but I need at least 6.2 amps worth of sunlight to do so on a single group 31 flooded battery at 130 amp hours rating, and I have a MeanWell RSP-500-15 adjustable voltage switching power supply which will do 40.94 amps into a depleted battery, and can be dialed upto( and well past) 16 volts, but is a manual charger and must be monitored, or put on a timer when set to absorption voltages.
https://vanlivingforum.com/showthread.php?tid=10873&highlight=my+newest+electrical+toy
Note Equalization voltages should only be applied to a battery which has seen at least 2 hours at battery manufacturer recommended absorption voltage. The charging source should not just blow past 14.x and goto 15.5 or 16V as this is abusive to the battery. EQ sessions are abusive themselves, but less abusive than chronically undercharging them or never equalizing them. So begin an EQ after a regular 'full' charge, and stop when the Specific gravity, temperature compensated, no longer rises, or battery electrolyte temperature approaches 120F.
Battery manufacturers are all over the map as to recommendations as to how often to perform an EQ charge, but basically the deeper the cycles and the more chronically undercharged the batteries are each charge cycle, the more important and the more often an EQ should be performed, and it will be different for everybody, their batteries and their usage of said battery.
After an EQ session, the maximum SG reading is the goal one hopes to approach at the end of 2 hours at absorption voltage. If 2 hours at 14.8v gets within 0.005 of the maximum then rezero the battery monitor at that point. 2 hours at 14.4v might do it too, or come nowhere close. It depends on the battery, as well as the charging source, as generally higher initial amperages do not require the extended time at higher voltages to max out SG in my observsations and experience. The point is that one needs to verify the full charge indicators various charging sources use, and can't blindly believe their trimetric or other battery monitor or blinking green light of other charging sources.
I've found my batteries, past and present, love a morning blast of alternator amperage in the 40 to 60 amp range, even if for only 20 minutes, then letting the solar finish them off. Basically the earlier in the day that the batteries reach ABSV, the better chance they have of achieving maximum specific gravity. I have also set my 'Float' voltage up higher than Absorption voltage and use it as a 'Finishing' or 'topping' charge. But If I do not cycle the battery the night before, then I reduce absorption voltage and duration and reduce float voltage to 13.2v, as a non cycled battery does not need to spend 2 hours at 14.8 and the rest of the day at 15.3v, but my deeply cycled flooded group31 battery certainly and overwhelmingly does require this.
I've really been using this battery hard, and it has obviously lost capacity, but a year ago when I first got it, I was applying more standard Absv's and durations and SG had tanked into the red and performance was Horrid after 10 cycles to 75% SOC. The hydrometer and raising voltages and durations and EQ charges allowed me to get this petulant battery to perform properly. If I did not take the time to figure this out, this battery would have been recycled long ago.
Most all battery systems would benefit greatly by verifying that the charging source is doing the job it claims to be able to do. Mine was no where near. Most systems are likely similar. Not an issue if you get to plug in and recharge, or stop cycling the battery and give the solar a few days to shoehorn in everything into a battery, but when the next discharge cycle begins before sundown that night, then it is of utmost importance to get the battery to near as possible to 100% before that next discharge cycle begins.
The clock is ticking, and full time dwellers have a different set of charging requirements than those who part time or who get to plug into the grid and let a charging source have days to perform the task the full time dweller needs done in hours.