Hi Everybody,
Last year I had an issue with my van where the alternator shorted out after a long drive with the house system connected to the vehicle system.
Recently, I upgraded my solar to a TriStar MPPT and while reading the manual to set the charge characteristics switches, I noticed there is one type of battery that does NOT have absorption or equalization phases and a constant voltage is maintained. That would be GEL type batteries.
Gel charging requires constant 13.7 v. The alternator will never go above 13.7. This will NOT correctly charge the other types of batteries. [I had wondered why the voltage from the alternator never went above 13.7. D'oh. I suspected the alternator was iffy.]
Connecting my house batteries with solar charging to the vehicle charging system did two bad things.
1. The house batteries were not being charged.
2. Worst thing, the vehicle's alternator was seeing the solar controller putting out 14.7 (in sunlight) to correctly charge the house batteries and over voltage to the Gel vehicle batteries.
The vehicle's alternator reacted by trying to reduce the 14.7 to 13.7. Which was impossible in this situation. I assume the alternator shunts to ground to reduce the extra voltage. The solar controller would put out more amps to keep the voltage up at 14.7.
Leading to Meltdown. Smoke was released.
The proper method with compatible charging and battery systems when connecting via a solenoid would be to use the extra terminals on the solenoid that do the opposite of the main terminals. When the main terminals are open circuit, not connected, the extra terminals are closed circuit. That way the charging systems could not influence the other.
In my case, the house and vehicle must never be connected electrically [unless I switch to house to GEL]. Vehicle is 2006 Ford E350 Super Duty.
Never assume.
Thanks for reading,
Wayne
Last year I had an issue with my van where the alternator shorted out after a long drive with the house system connected to the vehicle system.
Recently, I upgraded my solar to a TriStar MPPT and while reading the manual to set the charge characteristics switches, I noticed there is one type of battery that does NOT have absorption or equalization phases and a constant voltage is maintained. That would be GEL type batteries.
Gel charging requires constant 13.7 v. The alternator will never go above 13.7. This will NOT correctly charge the other types of batteries. [I had wondered why the voltage from the alternator never went above 13.7. D'oh. I suspected the alternator was iffy.]
Connecting my house batteries with solar charging to the vehicle charging system did two bad things.
1. The house batteries were not being charged.
2. Worst thing, the vehicle's alternator was seeing the solar controller putting out 14.7 (in sunlight) to correctly charge the house batteries and over voltage to the Gel vehicle batteries.
The vehicle's alternator reacted by trying to reduce the 14.7 to 13.7. Which was impossible in this situation. I assume the alternator shunts to ground to reduce the extra voltage. The solar controller would put out more amps to keep the voltage up at 14.7.
Leading to Meltdown. Smoke was released.
The proper method with compatible charging and battery systems when connecting via a solenoid would be to use the extra terminals on the solenoid that do the opposite of the main terminals. When the main terminals are open circuit, not connected, the extra terminals are closed circuit. That way the charging systems could not influence the other.
In my case, the house and vehicle must never be connected electrically [unless I switch to house to GEL]. Vehicle is 2006 Ford E350 Super Duty.
Never assume.
Thanks for reading,
Wayne