Batteries in parallel

Van Living Forum

Help Support Van Living Forum:

MJRW

Well-known member
Joined
Oct 30, 2019
Messages
57
Reaction score
4
I have 2 AGM 12V 125ah batteries I want to use parallel. They are right next to each other (so wire to be <a foot). 1200 watt inverter (more than I'll likely need), 50 amp MPPT/DC-DC charger, 3x100 watt solar panels, 12V refrigerator (plus usual led lights, fan, charging ports). Question: the 2 cables (+/-) should be what gauge? The inverter came with 4 gauge. The guy at local NAPA said that would do for joining the batteries as well. I read other on-line comments saying you need much bigger cables for the batteries. I find the wire sizing charts confusing. Can someone experienced  just tell me what size I need?
 

MJRW

Well-known member
Joined
Oct 30, 2019
Messages
57
Reaction score
4
[font=Tahoma, Verdana, Arial, sans-serif]Don't know why my post (above) was cut off. Here it is in full:[/font]

[font=Tahoma, Verdana, Arial, sans-serif]I have 2 AGM 12V 125ah batteries I want to use parallel. They are right next to each other (so wire to be <a foot). 1200 watt inverter (more than I'll likely need), 50 amp MPPT/DC-DC charger, 3x100 watt solar panels, 12V refrigerator (plus usual led lights, fan, charging ports). Question: the 2 cables (+/-) should be what gauge? The inverter came with 4 gauge. The guy at local NAPA said that would do for joining the batteries as well. I read other on-line comments saying you need much bigger cables for the batteries. I find the wire sizing charts confusing. Can someone experienced  just tell me what size I need?[/font]
 

MJRW

Well-known member
Joined
Oct 30, 2019
Messages
57
Reaction score
4
Happened  again! Why can't I post it all?  I've posted successfully before.
 

B and C

Well-known member
Joined
Dec 8, 2014
Messages
5,283
Reaction score
14
Location
Atascocita, TX
The wire size tying batteries together has to be a minimum size able to handle your highest draw. Most people use 4 Ga unless you're connecting a large inverter. Be srue to connect your positive load/charge to one battery and the negative to the other battery.
 

Weight

Well-known member
Joined
Feb 27, 2017
Messages
2,157
Reaction score
8
It is best to use large cable sizes to connect the batteries, either series or parallel as yours. I would never use less than 2/0 cable between batteries. The main objective is to reduce voltage drop in the battery bank. Then, The individual devices can be wired with the smaller awg if appropriate for their ampere draw. And fuses at the positive battery terminal.
 

MJRW

Well-known member
Joined
Oct 30, 2019
Messages
57
Reaction score
4
When you say fuses (plural) at the + terminal, you don't mean BOTH + terminals do you?
 

B and C

Well-known member
Joined
Dec 8, 2014
Messages
5,283
Reaction score
14
Location
Atascocita, TX
Anything connected to positive needs a fuse as close to the battery as feasible except for the cables tying the batteries together. It just becomes one bigger battery at that point.
 

Weight

Well-known member
Joined
Feb 27, 2017
Messages
2,157
Reaction score
8
What B&C said. I take my battery to bus bar. Fuse at bus bar for any branch circuits.
 