Exactly!RogerD said:In cool mode, it showed .48 amps when the compressor wasn't running and up to 3.6 amps when it was running. The amps being used fluctuates, so I can't just do 3.6 X 10.
Same with watts, which is just times V to get A.
That is why
> What I do know is how many watts of power was used to run the unit for the time frame it ran.
> it used 1500 watts in cool mode to run for 5.5 hours.
are not correct.
Only watt-hours (or AH) make sense with the "per 5.5hours"
And that is why a specialized AH/wH counter is needed, it "integrates" - like the area under a curve in calculus - all the different instantaneous watt/amp flow rate readings to give an accumulated wH/AH total per time period
> Watts divided by volts is supposed to equal amps. 1500 / 12 = 125 amps
You need wH divided by volts (13 closer IRL) to get AH.
> I'm assuming that the 125 amps used that it took to run the unit for 5.5 hours is the same as 125 battery amp hours
If that 125 **AH** was at 110VAC, then at around 13VDC it would be around 10x, or 1250AH.
Stick with wH for consistency, only use AH when voltage is clearly known to all in the discussion.
Plus note the big inverter involved in the DC-to-AC conversion will also consume a fair bit of power.