I am wanting to build a battery bank using my 2 200AH Renogy batteries. The entirety of my electrical setup is as follows:
300w of solar
Renogy MPPT charge controller
4000w inverter
2 200AH Renogy AGM Batteries
My max load should be 2000w from my induction cooktop, most of the time if I use the cooktop I'd be using it at lower wattages. I don't have any other appliances that come close to using that much energy.
Trying to figure out what wire gauge I need to connect the batteries in parallel (so that it will be a 400ah 12v bank). The inverter came with some 3 ft 0 AWG cables, and I would like to know if those are ok to use with the cooktop or if I'll need an upgrade for that 2000w load.
Right now I have some 1ft 4/0 AWG cables coming and the plan is to use those to connect the batteries.
The oversized bank is because I spend some time in areas where it gets cloudy often - but the sunny days usually leave me with excess power that could be stored in the larger bank. I want to get it set up to charge from the alternator soon as well but haven't done it yet.
300w of solar
Renogy MPPT charge controller
4000w inverter
2 200AH Renogy AGM Batteries
My max load should be 2000w from my induction cooktop, most of the time if I use the cooktop I'd be using it at lower wattages. I don't have any other appliances that come close to using that much energy.
Trying to figure out what wire gauge I need to connect the batteries in parallel (so that it will be a 400ah 12v bank). The inverter came with some 3 ft 0 AWG cables, and I would like to know if those are ok to use with the cooktop or if I'll need an upgrade for that 2000w load.
Right now I have some 1ft 4/0 AWG cables coming and the plan is to use those to connect the batteries.
The oversized bank is because I spend some time in areas where it gets cloudy often - but the sunny days usually leave me with excess power that could be stored in the larger bank. I want to get it set up to charge from the alternator soon as well but haven't done it yet.