John61CT said:Sounds right.
You happy with the unit so far, how long you had it?
John61CT said:Is that charging an LFP bank as per the thread title?
John61CT said:OK good.
When amps into the bank fall below 1A per 100AH, that is the definition of 100% Full. Unless mfg specs a different tailing amps rate like .005C or .015C
Can you tell the meter that, manually reset it to 100%?
John61CT said:So as I thought, that meter is **only** using voltage for (roughly) estimating SoC.
Not saying that's bad, certainly simpler for users.
So when you see the tailing amps drop below your more accurate Full point, note the voltage at that time, if SoC is below 100%, drop the full voltage setpoint until the gauge is calibrated.
Do you have 0% set to 10.5V?
John61CT said:As long as loads are less than charge source amps no current is drawn from the batt, but only a shunt at the batt knows what it is absorbing.
The charge source usually has an egg timer to hold Absorb, you need to calibrate that based on max or avg loads.
If your bank is 300AH then .005C is 1.5A
Check mfg specs, that endAmps spec can vary.
Set charger to hold at mfg spec'd Absorb V, terminate at endAmps, let bank rest a few hours isolated, that is then "100% Full" voltage.
Yes 10.5V is 0% SoC for lead, you only want to get there (briefly) for controlled maintenance or testing protocols.
Will be interesting to set AH capacity properly, then draw down to gauge says SoC 50% compare to AH out.